Hey all, had a quick question regarding an external distribution panel. A family member asked me to help get power to a very small garage 10x20. Only needing a few outlets 2 lights and a garage door opener. First option was to pull off of a 40amp breaker in his basement out of his 200amp panel but that's not very easy at all and would be about 400 feet away. Other option was to run new service. But they run minimum of 200 amp and charge more monthly for the meter than he would use. So my last option and I'm hoping it is alright, would be to set an outdoor service panel just beside the meter base and have a 200amp main with a 200amp circuit to the house and a 60 to run the shed wich is about 20ft from the base. Then I can just throw in a small 60amp sub panel in the shed. One, is this allowed and 2, does this change my bonding location? Would I bond it at the new service panel and remove the bonding screw from the main in the basement and follow sub panel rules regarding this? Also location is in Indiana and we just have to have a licensed electrician give the ok before service is restored.