rlqdot
Member
- Location
 - St. Louis, MO - USA
 
- Occupation
 - Professional Engineer (multiple states) - building design
 
is it permissible under NEC 240.21(B)(5) to extend a 70 amp 208/3 volt feeder from a circuit breaker inside a building underground to an outdoor wireway, then tap that feeder with two 20 amp taps and one 30 amp tap which each terminate in its own circuit breaker.  feeding a septic treatment "plant" with three controllers - two 20 amp, 2-pole (208/1 volt) controllers and one 30 amp (208/3 volt) controller.  feeder would be #4 (or #3 depending on voltage drop), taps would be #12 and #10 conductors.  i can't tell if 240.1(B)(5) dictates the location of the line-end circuit breaker or the load-end circuit breaker.
	
		
			
		
		
	
				
			
				