rc1agr2
Member
- Location
- Tavares, FL, USA
In reading NFPA 37, Section 4.1.1; it says the minimum separation shall not be required if you meet item 1. Adjacent wall of structure is 1 hr rated. and 2. the weatherproof enclosure on the generator is noncombustible.
Does this include the opening spacing requirement of 5ft?
If the opening is a solid window (non operable) in a masonry wall, is this still considered an opening?
Does this include the opening spacing requirement of 5ft?
If the opening is a solid window (non operable) in a masonry wall, is this still considered an opening?