Outside Taps of Unlimited Length

Status
Not open for further replies.

camaelec

Member
A feeder starts at a switchboard with a 225A breaker and runs underground with #4/0 copper THWN conductors. In an underground pullbox, a tap is made with #3 copper THWN conductors. These #3 conductors continue underground for 200 feet and rise in a small storage building to a panel with a 70A main breaker. The conductors are protected in conduit their entire length except for the tap in the pullbox, which has a locking lid.

Does this installation conform to the outside tap rule described in NEC Article 240.21(B)(5)?

Edited to remove the e-mail address. Please use the Private Messaging system to trade e-mail addresses. Thanks, Charlie

[ November 22, 2004, 07:42 PM: Message edited by: charlie ]
 