main197
Member
- Location
- California
- Occupation
- EE
240.21(B)(5) says that taps can be of unlimited length if the conductors are located outside of a building or a structure, except at the point of load termination, and meets four conditions. The handbook says it is somewhat similar to the installation of service conductors where conductors are fed from outside and into a building without limitations on tap conductor length.
My question is, what if it's the other way around? If a panel located inside a building is bus tapped and the conductors feed another panel located outside the building, can the conductors be of unlimited length (assuming it meets all four conditions)?
My question is, what if it's the other way around? If a panel located inside a building is bus tapped and the conductors feed another panel located outside the building, can the conductors be of unlimited length (assuming it meets all four conditions)?