Oven owners manual /Incorrect information :0

Status
Not open for further replies.

sparks27

Member
Location
Portland, Oregon
Why do they bother printing this information?
Contractor says he can put this on a 40 amp 2 pole breaker, with number 8 thhn
Instructions say its ok, they read it, and don't see a problem "the oven works fine"
 

Attachments

  • !cid_C7E61268-916D-4895-989E-0919A944A43B.jpg
    !cid_C7E61268-916D-4895-989E-0919A944A43B.jpg
    145 KB · Views: 0
The spec sheet shown is for a range not just an oven. A 40 amp circuit would be correct size for the 14.3kw nameplate range. See 220.55 for sizing range circuits.
 