oven requirements

JoeNorm

Senior Member
Location
WA
I'm installing a stand alone single oven. They call it a 4.2KW unit and specify a 30amp breaker. The fixture whip(hard wired) is #12 stranded.

So I am thinking running #10 will be more than adequate but the manual calls for #8. Is there any justification for this?

Not only does it call out #8 but it says #8 solid wire, which I am not sure if I have ever even seen.

I normally defer to manufactures specs like I am supposed to but in this case I am questioning them. Thoughts?
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
I'm installing a stand alone single oven. They call it a 4.2KW unit and specify a 30amp breaker. The fixture whip(hard wired) is #12 stranded.

So I am thinking running #10 will be more than adequate but the manual calls for #8. Is there any justification for this?

Not only does it call out #8 but it says #8 solid wire, which I am not sure if I have ever even seen.

I normally defer to manufactures specs like I am supposed to but in this case I am questioning them. Thoughts?
The only #8 solid I have ever seen was bare for grounding/bonding use.

Mark
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Do you have a link to the instructions? The 30 amp circuit is fine. Why they would require #8's for a 30 amp circuit is beyond me. Also the #12 wire in the whip is fine because it typically is a much higher temperature rated wire than THHN and the manufacturer can use conductors smaller than those required by the NEC. Good luck trying to find a cable with #8 solid.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I was thinking since the resistance (heating elements) were the same you would figure it the same.
To do that, determine the load's resistance (the constant), then calculate the new current (the result) on the new voltage (the variable).

Remember, a resistive load actually has a fixed resistance, not a fixed power. The rated power is a result of applying a certain voltage.
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
To do that, determine the load's resistance (the constant), then calculate the new current (the result) on the new voltage (the variable).

Remember, a resistive load actually has a fixed resistance, not a fixed power. The rated power is a result of applying a certain voltage.
I'm not sure I would call a heating element a "fixed resistance" value. The resistance goes up as the heat goes up, just like a light bulb. Please tell me if I'm missing something, I probably am.

Mark
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I'm installing a stand alone single oven. They call it a 4.2KW unit and specify a 30amp breaker. The fixture whip(hard wired) is #12 stranded.

So I am thinking running #10 will be more than adequate but the manual calls for #8. Is there any justification for this?

Not only does it call out #8 but it says #8 solid wire, which I am not sure if I have ever even seen.

I normally defer to manufactures specs like I am supposed to but in this case I am questioning them. Thoughts?
Is there a UL label? 8 solid in romex or se I have never seen.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I'm not sure I would call a heating element a "fixed resistance" value. The resistance goes up as the heat goes up, just like a light bulb. Please tell me if I'm missing something, I probably am.
Compared to cold, I'm sure you're right, but I doubt there's much difference between 240v and 208v.
 

JoeNorm

Senior Member
Location
WA
I actually cannot remember the brand right now. To be clear, I already ran #10 so I am choosing to ignore the specs.

I just thought I'd ask here to see if anyone has seen oddball requirements like that.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
I'm not sure I would call a heating element a "fixed resistance" value. The resistance goes up as the heat goes up, just like a light bulb. Please tell me if I'm missing something, I probably am.

Mark
I think you meant "as the temperature goes up".
You're not missing anything about the physics; they're spot on. But it appears your editor was asleep at the switch.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Probably Chinese made. I had an Italian engineer want 5/0 wire to a machine I was installing! Maybe they make 5/0 in Italy, but sure haven’t seen it here! LOL!
 