I have 11kw, 208V, three phase, 31A Blodgett model SHO-100-E oven. The drawing shows nema 15P-50 receptacle with 50A overcurrent protection to the receptacle.

Is 50A breaker too big for the oven? If yes then which code section? If no then which code section?
 
I have 11kw, 208V, three phase, 31A Blodgett model SHO-100-E oven. The drawing shows nema 15P-50 receptacle with 50A overcurrent protection to the receptacle.

Is 50A breaker too big for the oven? If yes then which code section? If no then which code section?

I agree with infinity. 40 amp breaker X .8 (80%)=32A & a 50 amp receptacle.
 
It's in the 2017:

210.8(B) Other Than Dwelling Units. All single-phase receptacles
rated 150 volts to ground or less, 50 amperes or less and three-
phase receptacles rated 150 volts to ground or less,
100 amperes or less installed in the following locations shall
have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens
(3) Rooftops
Exception: Receptacles on rooftops shall not be required to be readily
accessible other than from the rooftop.
(4) Outdoors
Exception No. 1 to (3) and (4): Receptacles that are not readily accessi‐
ble and are supplied by a branch circuit dedicated to electric snow-
melting, deicing, or pipeline and vessel heating equipment shall be
permitted to be installed in accordance with 426.28 or 427.22, as
applicable.
Exception No. 2 to (4): In industrial establishments only, where the
conditions of maintenance and supervision ensure that only qualified
personnel are involved, an assured equipment grounding conductor
program as specified in 590.6(B)(3) shall be permitted for only those
receptacle outlets used to supply equipment that would create a greater
hazard if power is interrupted or having a design that is not compatible
with GFCI protection.
(5) Sinks — where receptacles are installed within 1.8 m
(6 ft) from the top inside edge of the bowl of the sink
Exception No. 1 to (5): In industrial laboratories, receptacles used to
supply equipment where removal of power would introduce a greater
hazard shall be permitted to be installed without GFCI protection.
Exception No. 2 to (5): For receptacles located in patient bed locations
of general care (Category 2) or critical care (Category 1) spaces of health
care facilities other than those covered under 210.8(B)(1), GFCI protec‐
tion shall not be required.
(6) Indoor wet locations
(7) Locker rooms with associated showering facilities
(8) Garages, service bays, and similar areas other than vehi‐
cle exhibition halls and showrooms
(9) Crawl spaces — at or below grade level
(10) Unfinished portions or areas of the basement not inten‐
ded as habitable rooms
 