It appears to be safe to post this now
I have a sight unseen dual fuel oven and I could wait to see the nameplate but I want to price the wire now.
Oven 1) Auxiliary Oven:
a)Bake Element 2600 watts
b)Broiler Element 3000 watts
Oven 2) Upper/Single Oven Settings:
c)Bake Element 1800 watts
d)Broiler Element 2200 watts
I assume I need to figure on both broiling elements being used at the same time for max load. (Dont think bake and broil cant be used at the same time)
3000+2200= 5200/240= 21.6 = #10 with 30 amp breaker correct? Panel is fairly close by. Web specs say 50 amps needed..Thx