I am installing a 4160V to 480V substation and have a question about 110.31. This enclosure is going outside in a fenced area. I think it is pretty clear that I need to conform to Table 110.31. But my assumption is the 10'-0" requirement only pertains to the front and rear of the equipment (since the equipment is front and rear access only) and does not apply to the sides. So I may have the fence right up against the sides no problem, but need the 10'-0" clear in the front and back. Is my interpretation correct?
Also, I believe I must comply with 110.31(C)(2) because the fence is locked, but I'm confused why it references 110.34, 110.36 and 490.24 and does not mention 110.32, 110.33 or 110.40. I'm assuming I still need to comply with 110.32 and 110.33, even though 110.31(C)(2) leaves these sections out. Is this correct?
Lastly, what is the difference between 110.31(C)(1) and 110.31(D)?
Forgot to add this -
110.33(A)(3) - Does this apply to gated and fenced areas?
Also, I believe I must comply with 110.31(C)(2) because the fence is locked, but I'm confused why it references 110.34, 110.36 and 490.24 and does not mention 110.32, 110.33 or 110.40. I'm assuming I still need to comply with 110.32 and 110.33, even though 110.31(C)(2) leaves these sections out. Is this correct?
Lastly, what is the difference between 110.31(C)(1) and 110.31(D)?
Forgot to add this -
110.33(A)(3) - Does this apply to gated and fenced areas?