zach_zachary1@yahoo.com
Member
- Location
- Apex,NC
I am installing two autoclaves in a lab. It takes 208v 3ph power and has a full load amp rating of 26 amps. It runs for less then 3 hours so it is a non continous load. Using 210.20 I specked a 30 amp breaker. According to 310.15(B)16 10 AWG wire is rated at 40 amps if I use THHN rated at 90 *C . I am going to have 6 conductors together because I installing two autoclaves. Using table 310.15(B)(3)(a) I down grade the amps on 10 AWG by 20%. 40 amps x 80% = 32 amps. I am going to use 1" RMC aluminium. Using Chapter 9 table 1, I can fill the conduit to 40%. I will be pulling 8 wires. 6 conductors and 2 grounds. According to my calculations I will only fill the conduit to 21%.
Does this look good to everyone?
Thanks!
Does this look good to everyone?
Thanks!