vtsoundman
- NorCal
There is something else going on here...a 20A breaker will often hold 110% (22A) for an hour. I know this from lots of testing of various breakers. Yes, breakers do become weak with multiple trip events - and Res'd breakers don't like being used as swtiches...
The OP needs to put a ammeter on the load that can capture both peak draw and RMS draw....assuming the wire isn't loose, undersized, or the breaker isn't getting hot from some other source, he's got a partial short (few of the heaters coil are done) or the motor is slowing cooking itself.
These things on a GFCI? If so, then you have a leakage issue. Did the blowers always do this? If not, then leakage (GFCI) or high impedance short become lower impedance with heat. Hot air blowers implies water...so to the OP, do screw around - get the repair tech in there and get it fixed right.
The trip curve for a 20A SqD Qo is below... assuming the breaker isn't trashed, @ 3min of running with a trip, my guess is your pulling >30A or more - most likely approaching 40A.
edit: can't post the image...click here instead