A 70 amp two pole breaker is rated at 70 amps for each leg is it not??
No, you did not confuse the answer at all. To the contrary, that is quite clear. I have a 70 amp 2P breaker running a heating load (head bolt heaters) and the actual dynamic amp load is 40 A, 23 A, and (34 A on the neutral). However the breaker keeps tripping. I am thinking now perhaps it is tripping on imbalance or perhaps I need a new 70 amp breaker.
At any rate I just wanted to know for sure that one does not add the amp readings together because if that is the way it worked then it would be obvious why the 70 amp breaker is tripping as it would have 97 amps on it.
Thank you Charlie B. and charlie E.
There is a formula that relates the neutral current to the current on the other phases, and these numbers are consistent with what that formula is telling me. So my guess is that you have a breaker that has failed, and the solution should require nothing more than a new breaker.. . . the actual dynamic amp load is 40 A, 23 A, and (34 A on the neutral). . . .
Normal circuit breakers (those without electronic components) do not trip on current imbalance.I am thinking now perhaps it is tripping on imbalance or perhaps I need a new 70 amp breaker.