Eduardo Maun
Member
- Location
- Qatar
I got 2000 kva transformer, 3 phase delta-delta, 11kv, 433v/220 system. I calculated the primary current and I got 2,666.75 ampere i find in the sample problem there is a factor of 1.67 after multiplying that factor i got 4,453.47 ampere my question(s) are: where the 1.67 came from is it a factor of what? by the way does my calculation is correct? for the secondary i got 5,248.64 ampere and when I multiplied the Is (Vs/Vp) according to NEC the primary can protect the secondary conductors if the Ip does not exceed to value of secondary conductor ampacity by the secondary to primary transformer voltage ratio. I use the voltage ratio as 433/220v. I know you can help me on this.
Thank you!!!
Thank you!!!