Well, to start with I don't see 200 kcmil conductors in table 310.16. But it seems that you are asking about the tap rules (240.21). Is that right?
Presuming that is your question, it all starts with the rule that every conductor must be protected against overcurrent, and most of the time the overcurrent device has to be located at the point at which the cable gets it power. That makes sense because if the conductor experienced a short circuit somewhere in the middle of the run, and if the overcurrent device was at the end of the run, the device would not be able to trip and protect the conductor.
The tap rules give us certain, specific conditions under which we can protect the conductor where it supplies its load, as opposed to where it gets its power. So to figure out what the max OCPD would be, you need to find out which of the tap rules applies to the situation.