Resistive Boiler supplies in floor heating for dwelling.
Boiler is rate 240 volt 1 phase 16KW.
No minimum branch circuit or maximum over-current.
Calculate load as continues as required in 424.3 125% 83 amps.
Load is subdivided and protect be 50 amp over-current devices.
Question is can provide single circuit # 2 CU THHN protect 100 amp breaker.
Or must OPC device be limited to the 125% calculation 90 amp