How is it possible to have a time over current / instantanous relay for a self contained 15 kv breaker trip only once for instantanous and then trip on time overcurrent? The breaker is 50 years old and the relay is an iac50/51. The reclosing timer is also located in the breaker and we block the instantanous part of this relay for down stream fuse coordination. I don't know why we block the instantanous if we are able to shut it off after it trips once. I was told this was possible.
 

newt

Senior Member
I want to unblock the inst. if there is a way to limit it to one trip and the rest go threw the time delay. So the down stream fuses will blow on time delay,and the inst. unblock will limit arc flash hazard for the lineman.
 

newt

Senior Member
Thanks I know we are able to do this with reclosures but wasnt sure about self contained breakers
 

rcwilson

Senior Member
Location
Redmond, WA
Check the Basler website for IAC plug in replacement relays. They package digital or solidstate analog relays that slide into the IAC can. They might have a model that could do this logic.