what size manual motor starter should one get for a 230v/ single phase/ 3hp. with a overload protection FLA is 16 amps... FLC is 17amps...SF 1.15..
no just want to make sure I did the equation right..
What you would get is a MMS that has a rating of 3HP. the amp rating is secondary to the HP rating, meaning that even if you think the amp rating is going to work, if it is not rated for 3HP or more, you cannot use it.
What you SET the OL trip for (or how you select OL heater elements) will depend on the specific instructions of that specific MMS that you purchase and how it is used, mounted etc..