Is it Ok to use over load relay on a feeder which is not motor?
Is it Ok to use over load relay on a feeder which is not motor?
The overload relay can be removed/bypassed if there is any concerns in that kind of application. Not too often is there anything to be concerned about other then if the load will be more then the trip setting. Many solid state overloads you have the range of the contactor rating to deal with. Many bimetal overloads, especially on small frame sizes, you may be able to get more out of the contactor then some of the overloads that work with it. Of course melting alloy thermal units need changed to get the setpoint desired, but is cheaper to remove or bypass then to purchase new elements.I would bet the OP has an existing motor-starter with overload unit and is asking about using it to switch other types of loads.
I would bet the OP has an existing motor-starter with overload unit and is asking about using it to switch other types of loads.
If you have a combination starter with magnetic trip only circuit breaker that was the situation where that applied. Not all combination starters will have a magnetic trip only breaker, some may have a inverse time breaker, some may have fuses, and some are just a non fused disconnect.It looks that I got the answer (240.9)
.... Not all combination starters will have a magnetic trip only breaker ... and some are just a non fused disconnect.
Code issues aside, that does not sound like good design. What is the short circuit protection?
Hummm ... didn't know that. I don't think I have ever seen a combination starter that did not have OCP ahead of the contactor - fuses, TM, mag-only.
Code issues aside, that does not sound like good design. What is the short circuit protection?
ice
May not be something convenient for most applications you run into, but they are out there. If you already have branch circuit protection, why do you need such protection a second time?The short circuit protection is the branch circuit breaker supplying the circuit.
Actually with the advent of more emphasis on proper SCCR ratings, this (non-fused disconnect type combo starters) is tending to go by the wayside now. Most NF disconnects are not rated very high for SSCR without the fuses and not series rated with breakers. So if you can only use them down stream of another fused disconnect, that makes them either pointless, or only applicable for use where you have a fused switchboard feeder, which are less and less popular. I do not know of any distributors that still stock them even if their manufacturer still offers them, then when you go to buy one you discover that you not only have to wait to get it, but it is no cheaper than a fused version or an MCP version. I just ran into that issue recently, went with the MCP version combo starter because it was on the shelf AND less expensive than the NF version!May not be something convenient for most applications you run into, but they are out there. If you already have branch circuit protection, why do you need such protection a second time?
Hummm ... didn't know that. I don't think I have ever seen a combination starter that did not have OCP ahead of the contactor - fuses, TM, mag-only.
Code issues aside, that does not sound like good design. What is the short circuit protection?
ice
The short circuit protection is the branch circuit breaker supplying the circuit.
May not be something convenient for most applications you run into, but they are out there. If you already have branch circuit protection, why do you need such protection a second time?
Exactly one scenario I have going on a project right now. Not a QOB, but close enough comparison, my install is EDB breakers instead of QOB's, and I need a disconnect either within site of the controller or within site of the motor. We chose to place combination starter within site of the motor in this case as controls are only needed at the motor location in this application so it is breaker at start of branch circuit - combination starter - motor. Pretty simple install.That would be true.
So an appliction might be a QOB panel with a bunch of 3p CBs each feeding a separate stand alone combination starter - the starter having a non fused disconnect to provide the disconnect insight of the controller?
ice
True for a disconnect only, throw a motor starter in the same cabinet and you have something that may require service or adjustment while energized.For us, a non-fused disc does not require the working space a fused unit would. As long as the door opens 90deg we are good. Check with your inspector before installation.