Is a overhead water or plumbing pipe allowed to be installed in an IT room? Thanks for your time.
C Cableman Member Nov 30, 2010 #1 Is a overhead water or plumbing pipe allowed to be installed in an IT room? Thanks for your time.
raider1 Senior Member Staff member Location Logan, Utah Nov 30, 2010 #3 I agree with Bob, but want to add that the NEC does prohibit water pipes from violating the required dedicated equipment space for any panelboards that may be in the IT room. Chris
I agree with Bob, but want to add that the NEC does prohibit water pipes from violating the required dedicated equipment space for any panelboards that may be in the IT room. Chris
R Real_Bostonian Member Location Eastern Massachusetts Nov 30, 2010 #4 In some installations (not just IT rooms) I've had inspectors require drip trays to be installed under nearby plumbing pipes.
In some installations (not just IT rooms) I've had inspectors require drip trays to be installed under nearby plumbing pipes.