J Jason Dunscombe New member Location Festus, MO., Jefferson county Dec 8, 2011 #1 Where in the code does it actually state that the maximum continuous load on an overcurrent device is limited to 80 percent of the device rating?
Where in the code does it actually state that the maximum continuous load on an overcurrent device is limited to 80 percent of the device rating?
W WorkSafe Senior Member Location Moore, OK Dec 8, 2011 #2 230.208 (B) maybe? (B) Enclosed Overcurrent Devices. The restriction to 80 percent of the rating for an enclosed overcurrent device for continuous loads shall not apply to overcurrent devices installed in systems operating at over 600 volts.
230.208 (B) maybe? (B) Enclosed Overcurrent Devices. The restriction to 80 percent of the rating for an enclosed overcurrent device for continuous loads shall not apply to overcurrent devices installed in systems operating at over 600 volts.
david luchini Moderator Staff member Location Connecticut Occupation Engineer Dec 8, 2011 #3 Try 210.20(A) for branch circuit OCPDs, 215.3 for feeder OCPDs, (and indirectly, 230.90(A) together with 230.42(A) for services.)
Try 210.20(A) for branch circuit OCPDs, 215.3 for feeder OCPDs, (and indirectly, 230.90(A) together with 230.42(A) for services.)