Hello,
I have been a long time reader, first time poster. I have a scenario that I have run into at work that I hope some of you out there can help me with.
I am constructing a hospital and I spoke with the electrical inspector here and he raised an issue. Our 27.6kV incoming switchgear does not have overcurrent protection on the incoming loadbreak switch. This technically contradicts the electrical safety code here where "Each consumer's service, operating unit of apparatus, feeder, and branch circuit shall be provided with overcurrent protection having adequate rating and interrupting capacity in all ungrounded conductors" through circuit breakers or fuses.
In the same switchgear we have 2 additional switches, one that actually feeds the hospital and is FUSED (thus protecting the downstream feeder), and another that is empty but ready to be fused for Phase 2.
I argued with the inspector that a fuse on the incoming switch would not actually do anything but protect the internal bussing connecting the incoming switch to the fused switch ( about 2 meters worth of copper bus) since the outdoor switchgear from the Hydro company is fused as well, so the incoming feeder is protected.Although he agreed, he said I would have to put in a written request to have my situation reviewed. Also, the max current that will enter the switchgear is 84Amps at 27.6kV.
Any thoughts on further ammo to my argument? Appreciate any feedback!
I have been a long time reader, first time poster. I have a scenario that I have run into at work that I hope some of you out there can help me with.
I am constructing a hospital and I spoke with the electrical inspector here and he raised an issue. Our 27.6kV incoming switchgear does not have overcurrent protection on the incoming loadbreak switch. This technically contradicts the electrical safety code here where "Each consumer's service, operating unit of apparatus, feeder, and branch circuit shall be provided with overcurrent protection having adequate rating and interrupting capacity in all ungrounded conductors" through circuit breakers or fuses.
In the same switchgear we have 2 additional switches, one that actually feeds the hospital and is FUSED (thus protecting the downstream feeder), and another that is empty but ready to be fused for Phase 2.
I argued with the inspector that a fuse on the incoming switch would not actually do anything but protect the internal bussing connecting the incoming switch to the fused switch ( about 2 meters worth of copper bus) since the outdoor switchgear from the Hydro company is fused as well, so the incoming feeder is protected.Although he agreed, he said I would have to put in a written request to have my situation reviewed. Also, the max current that will enter the switchgear is 84Amps at 27.6kV.
Any thoughts on further ammo to my argument? Appreciate any feedback!