Can anyone provide some clarification on this? I think am pretty sure I know the answer but I would like some other opinions.
I have a 3-wire feeder (1-phase + nuetral) that leaves a 100A disconnect switch at the main service. The 100A disconnect is tapped off a gutter fed by an 800A main disconnect.
The engineer is specify # 3 THHN/THWN be installed a cross a roof to refeed an existing 100A panel located in an existing unit. Since these conductors will run across the roof, I have performed the required ampacity adjustments based on 310.15 (B)(3)(c). I am coming up with a corrected ampacity of 94.3 amps for these conductors (# 3 THHN = 115A x .82 adjustment factor per Table 310.15 (B)(2)(a)).
I can still install 100A fuses in the service disconnect to protect these conductors based on 240.4(B) correct? Or since the conductors have had an ampacity adjustment, they can now not exceed 100A? So I would need to install 90A fuses instead. I pretty sure that I can still install 100A fuses for protection, right?
I have a 3-wire feeder (1-phase + nuetral) that leaves a 100A disconnect switch at the main service. The 100A disconnect is tapped off a gutter fed by an 800A main disconnect.
The engineer is specify # 3 THHN/THWN be installed a cross a roof to refeed an existing 100A panel located in an existing unit. Since these conductors will run across the roof, I have performed the required ampacity adjustments based on 310.15 (B)(3)(c). I am coming up with a corrected ampacity of 94.3 amps for these conductors (# 3 THHN = 115A x .82 adjustment factor per Table 310.15 (B)(2)(a)).
I can still install 100A fuses in the service disconnect to protect these conductors based on 240.4(B) correct? Or since the conductors have had an ampacity adjustment, they can now not exceed 100A? So I would need to install 90A fuses instead. I pretty sure that I can still install 100A fuses for protection, right?