In a 480V motor control bucket with 120V control circuit, should the 480V/120V transformer be fused on the primary side? would an UNfused transformer (primary side) increase the risk of the transformer burning up/catching fire?
All of the buckets here are over 30 years old and none are fused on the primary side.

Thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In a 480V motor control bucket with 120V control circuit, should the 480V/120V transformer be fused on the primary side?
In general terms, yes , normally...see 430.72
That said, as a "factory" bucket it need only be built to the "standard" under which it was listed/labeled. (UL, etc)
At time of manufacturer, it may not have been required.
would an UNfused transformer (primary side) increase the risk of the transformer burning up/catching fire?
my opinion, yes
.