timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
I have a question about location of breaker for battery-conductors. NEC 240.21 states that the breaker has to be located at the starting point of the cable.
The breaker for battery-conductors acts both ways. Under normal conditions, the supply-source would be the charger. But when the charger is out of service, the supply-source would be the battery itself, which is on the opposite side of battery-conductors.
240.21(H) states that for battery-conductors, the breaker is permitted to be installed as close as practicable to the battery terminals in classified location. What does it mean, does it mean that the breaker can be located away from the battery (in some other room)? What do you guys think about it? Thanks.
The breaker for battery-conductors acts both ways. Under normal conditions, the supply-source would be the charger. But when the charger is out of service, the supply-source would be the battery itself, which is on the opposite side of battery-conductors.
240.21(H) states that for battery-conductors, the breaker is permitted to be installed as close as practicable to the battery terminals in classified location. What does it mean, does it mean that the breaker can be located away from the battery (in some other room)? What do you guys think about it? Thanks.