Re: Overcurrent Protection for Panelboard
First, we need to look at 368.12 which requires that the conductors that tapped off of the busway have overcurrent protection. In general this requires that the bus tapping device have an OCPD that will protect the conductors at their ampacity. However, Exception #1 permits the rules in 240.21 to be used. It appears from the information that 240.21(B)(1) would apply. The panel is rated at 400 amps, so 240.21(B)(1)(1) would require that the ampacity of the conductors between the busway and the panel be at least 600 kcmil copper. If the conductors are of this size or larger and the calculated loads served by the panel are 400 amps or less then the tap conductors do not require over current protection. If the conductors are smaller than 600 kcmil, an OCPD would be required at the bus tap. This brings us to the protection of the panel itself. 408.16(B) requires that this panel be protected at its ampacity either within the panel or anywhere on the line side of the panel. This requirement for overcurrent protection of panel is triggered because the panel has a neutral and more than 10% of the OCPDs installed in the panel are rated 30 amps or less. If the 20 amp breakers were 40 amp devices, neither the tap conductors nor the panel would require overcurrent protection.
Don
[ August 30, 2003, 01:05 PM: Message edited by: don_resqcapt19 ]