Hello,
How to size O.C device for small motors such as 1/8HP, 1/20HP etc.? I don't see manufacturer's recommended sizing on these motors.

Thank you.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
+ the GFSC protection on the small motors is normally the branch circuit breaker (See 430.53)
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
If you see the Thermally Protected on the nameplate the installation became very simple, just need GFSC and a disconnect
 