• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Overcurrent Protection for Small Motors

aelec84

Member
Location
Los Angeles
Occupation
Electrical Engineer
Hello,
How to size O.C device for small motors such as 1/8HP, 1/20HP etc.? I don't see manufacturer's recommended sizing on these motors.

Thank you.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
+ the GFSC protection on the small motors is normally the branch circuit breaker (See 430.53)
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
If you see the Thermally Protected on the nameplate the installation became very simple, just need GFSC and a disconnect
 