I have condensor unit with nameplate MCA: 24A MOPD: 25A. Can I use 15A overcurrent protection circuit breaker?
It says the following MCA Air: 15, MCA Elec24, MOPD Elec: 25. What minimum size overcurrent protection beI can use?
What is this that lists two different MCA?
I would still say 25 amp minimum.
I have condensor unit with nameplate MCA: 24A MOPD: 25A. Can I use 15A overcurrent protection circuit breaker?