We are replacing an air handler on a high rise building. The existing air handler is fed off of a 208V switchboard with an 800A breaker. However, the wires that were installed have an ampacity of just 500A. I am assuming this is because of motor load rules that allow for the overload in the air handler starter to act as the overcurrent protection.
The new unit we are providing has an MOCP of 450A and the owner was planning on just reusing the existing circuit. Question is can we simply install a 450A fuse ahead of the air handler or must the breaker at the switchboard be replaced?
I had thought the OCPD protects the feeder so I personally did not think the 800A breaker at the switchboard would be acceptable.
The new unit we are providing has an MOCP of 450A and the owner was planning on just reusing the existing circuit. Question is can we simply install a 450A fuse ahead of the air handler or must the breaker at the switchboard be replaced?
I had thought the OCPD protects the feeder so I personally did not think the 800A breaker at the switchboard would be acceptable.