Is there a requirement (similar to 408.36) that requires an OCPD having a rating of not-greater-than that of the transfer equipment that it protects? I really feel like there should be, but I have not been able to find one.
Consider a situation where a generator has a 250 amp breaker feeding a 200 amp rated transfer switch. You could theoretically run a 250 amp feeder from genset-to-ATS, so the conductors would be protected. What I'm not sure about is if the overcurrent protection for the ATS is required by the NEC to be rated equal-to or less-than that of the ATS, much like the requirement in 408.36 regarding ocpd for panel boards.
Consider a situation where a generator has a 250 amp breaker feeding a 200 amp rated transfer switch. You could theoretically run a 250 amp feeder from genset-to-ATS, so the conductors would be protected. What I'm not sure about is if the overcurrent protection for the ATS is required by the NEC to be rated equal-to or less-than that of the ATS, much like the requirement in 408.36 regarding ocpd for panel boards.