I have cell tower site in which cabinet houses rectifiers and AC side draws 63A continuous load. So the breaker should 63x1.25=78.7A be sized 80A however it is sized 150A. The reason is future expansion.
When I look at NEC2014 210.20 it says minimum breaker size but not for table 240.3 equipment but don’t see rectifier cabinet. Can the breaker be sized 150A or needs to be 80A?
When I look at NEC2014 210.20 it says minimum breaker size but not for table 240.3 equipment but don’t see rectifier cabinet. Can the breaker be sized 150A or needs to be 80A?