I am involved with the design of a renovation to a building that functions as an entertainment venue. To complete our construction documents we included a power riser diagram that described the existing system and included information regarding existing feeders. Well, one of the feeders we described was a 2000 amp feeder made up of 5 sets of 500kcmil copper which has an ampacity of 1900 amps. Again, all of this information was related to existing conditions and was taken from the original design documents completed in the mid '80's when the building was built. My plan reviewer's only electrical comment was that this existing feeder does not meet 2008 NEC 240.3 (C) which obviously it does not. I do not have access to any old code books but I was wondering if anyone else does. I am wondering if the NEC (late 70's to mid '80's) permitted you to go to the next higher standard overcurrent device rating above the ampacity of the conductors being protected as in 240.3 (B). I am planning on verifying the fuse size protecting this feeder but am anticipating that they will be rated for 2000 amps, just as the original plans called for. Any input would be appreciated.