A client is questioning whether the following meets NEC:
48 KW heater consisting of three 16KW delta heaters in parallel, total load 60A
Main feed #4 through 80A breaker and 74A overload
After overloads splits into three short runs of #10 (maximum wire size for heater termination)
The wire is sized per code table 310.15(B)(16) with applicable temperature derate.
I'm thinking section 240.21 allows this based on the short heater tap length.