A 150KVA transformer set on a pad to supply power to a new restaurant. From the transformer the wire is run parallel with 3/0 to a 600AMP main disconnect with 600AMP fuses mounted on outside of building. From the disconnect it runs to a single 350KCMIL 400AMP disconnect in panel box mounted inside electrical room. Would the 600AMP or 400AMP disconnect be the overcurrent protection? What is the sufficiant wire sizes for this service and the overcurrent protection requirement? This service is also 3phase.
My interpretation is that:
75C (degrees) at 600AMP you would use parallel 350KCMIL or 1500KCMIL and for 400AMP you would use parallel 3/0 or 600KCMIL.
90C (degrees) at 600AMP you would use parallel 300KCMIL or 500KCMIL and for 400AMP you would use parallel 3/0 or 500KCMIL.
This is probably very confusing and easier to explain, but if you understand any help would be very appreciative.