Re: Overfusing - why was this allowed???
To respond to the various questions/comments:
Gene: Size of service conductors appears to be #6 AL. I need to get a better look to be sure, but they don't appear to be the #2 AL they need to be for 100A.
Physis: As for disconnects, you'd effectively have three? the 60A for the bus, 40A for the stove, 30A for A/C.
GG: Thinking that this was the case for the A/C, but my friend who's owned the place since new says "no". Another reason I think that your guess is right is that the feed to the line side of the 30A fuse is only #10 CU. This is definitely not to code, seeing as you have no upstream circuit protection, and basically go from the service conductor to the #10.
JWElectric (1st): Agree? this meets the six disconnect rule.
Rick Hart: 100A would make me happy too. Unfortunately, I have NO idea how the service was run. Picture a long condo complex, meters on one side, my friend's condo on the other. The service appears to neither be run in conduit in the walls (since it's not individual conductors, but service entrance cable with no sign of any conduit), or run to the exterior and run underground (due to the orientation and height the cable leaves the panel, relative to the exterior of the condo). I'm thinking that it may have been run through the walls through the other adjoining condos. I do have to admit I have not looked at the meter bank, but I have a sneaking suspicion that there are no safety disconnects at the meters either.
Gene/Jwelectric (2nd): The panel is truly rated for 100A, but what I'm not seeing is? if the cable isn't rated for 100A, and you effectively have 60A, 40A, and 30A loads, how is this allowable?
Physis: Exactly. The way this box is wired, the service entrance conductor gets split between a 60A main fuse (that feeds the plug-in fuses below it), a 40A stove fuse, and a 30A A/C fuse. Thus, the stove and A/C fuses are not fed by the 60A main? but are tapped off the lugs on the line side of the 60A main.