Hello,
If I have a motor that is connected to a drive and it is for a crane application, I can have an idea of what the currents on the output of the drive would be as well as input of the drive.
If I require 100% torque for the load to pick it up and go rated speed, I would see roughly the rated current on the output of the drive and slightly less current on the input of the drive due to PF difference.
Now if I need 120% torque to get the load going to rated speed, I would again expect to see something of a 1.20x relationship on the output of the drive and similarly on the input of the drive from the rated values (ignoring that its not exact since the torque producing current would be the one being multiplied by 1.2 and through vectoral arithmetic the resultant current would be slightly less).
If I decide now to run the motor at 50% speed but at rated load, I can expect the same current on the output but roughly 50% current on the input. Due to the voltage remaining the same on the input but different voltage on the output and the application being a constant torque application.
Now, what happens on the lowering and the load becomes overhauling?
Say I am lowering the load at rated speed but the load becomes overhauling and the load begins to move faster than what the motor is telling it to go? (like car engine going down hill). The drive will have its DC bus voltage begin to raise. The chopper circuit will turn on an begin to dump energy into the dynamic braking resistor.
What is the input current to the drive? What is the output current to the drive?
How does that change when at 150% overhauling torque?
How does that change when at 50% speed?