Almost New install, It has 2 motors (480v 3P), one for lifting the other for moving it side to side. I haven't been able to talk to any of the people that got shocked. They were all contractors and they reported it to the plant supervisor before leaving.
I have checked all of the wires for bare spots. Ohm-ed them all to ground. I checked for voltage between the control support cable and a box on the wall and I got 24v AC. I added a ground wire to the control transformer and it dropped to 11v. The only thing I can come up with is the rail is painted and not allowing a good ground connection. Any ideas?
I have checked all of the wires for bare spots. Ohm-ed them all to ground. I checked for voltage between the control support cable and a box on the wall and I got 24v AC. I added a ground wire to the control transformer and it dropped to 11v. The only thing I can come up with is the rail is painted and not allowing a good ground connection. Any ideas?