jjhoward
Senior Member
- Location
- Northern NJ
- Occupation
- Owner TJ Electric
Detached garage is 60' from the house.
Overhead feed is now 10/2 UF tied to ceramic clevis type supports at both the house and the garage.
(Tied like a bow on a present. No messenger wire, no UV listing for the cable.)
This feeds an 8 position MLO panel.
To upgrade this garage feed I can use UF on a messenger wire from the house to the garage. (Table 396.10)
At the point of attacment at the garage must I end the UF and splice it to SER type cable, or can I terminate the UF in the garage panel since this is branch circuit and not a service feed?
And I will be installing 1 8' grnd rod attached to grnd bus of sub panel.
Thank you all.