It's important to note that this is a misstatement. Under previous cycles, you don't "run an EGC or drive a ground rod".Do i need to run a equipment grounding conductor with the tri-plex or could i drive a ground rod at the sub panel?
ptonsparky said:Some will say two rods.
Is the triplex UL listed?JustinFWE said:I have a detached garage. I am running a overhead feed from the main home panel to the sub panel of the garage. This is a single phase system. Do i need to run a equipment grounding conductor with the tri-plex or could i drive a ground rod at the sub panel?
JustinFWE said:I have a detached garage. I am running a overhead feed from the main home panel to the sub panel of the garage. This is a single phase system. Do i need to run a equipment grounding conductor with the tri-plex or could i drive a ground rod at the sub panel?
Ken 6789 said:on the quadruplex is the neutral identified on the cable or do you have to meter it out? the bare wire is the egc of course.
In aerial quadplex, unlike SPT cable, the neutral is generally the one without the "rib" on the conductor insulation.Ken 6789 said:on the quadruplex is the neutral identified on the cable or do you have to meter it out? the bare wire is the egc of course.