A client wants me to run a feeder to a 2nd shed from a subpanel in an adjacent outdoor shed. The adjacent shed is being fed from the service panel, and is coming off the house from an aerial cable over to the shed's subpanel. When I opened the panel to check spacing, I found no EGC.
Looking at the aerial cable, I only see 3 wires - two hots and a neutral. No EGC. Is this allowed? To have NO EGC for a feeder running from the service panel to an outdoor shed?
If I pull a feeder from the 1st shed subpanel to power the 2nd shed, how will there be any ground fault path back to the utility service without an EGC from the service panel to the 1st shed subpanel?
Attached are pictures of the current setup.