Overhead feeder with welder

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
We have an 480 volt ungrounded delta overhead feeder with a process spot welder and various other pieces of equipment on a piece low voltage switchgear. This is wired with 4/0 cable the gear is set up for long time trip at 400amp. When the spot welder is welding for brief 1 second intervals the current jumps to about 600amps. This is well above the rating of this wire is there any code provision that makes using this wire compliant at this rating. I cannot think of any.

Thanks
Dave
 