Can Triplex be used for an overhead 3 wire feeder utilizing the messenger as the neutral? This is replacing an existing feeder that utilized three individual conductors.
Do you really mean feeder as opposed to service?Can Triplex be used for an overhead 3 wire feeder utilizing the messenger as the neutral? This is replacing an existing feeder that utilized three individual conductors.
Do you really mean feeder as opposed to service?
Three wires for a feeder would be one hot, one neutral and one ground.
Triplex for 120/240 service would use the messenger as the neutral with no separate ground, yes?
Yes, this a feeder from one building to another. I'm thinking Triplex, 2 insulated ungrounded conductors and one bare grounded conductor. (Messenger). 120/240V. Just not sure if the grounded conductor needs to be insulated.
The NEC requires an EGC for a feeder. What will you do for that? Triplex is traditionally used for service wiring only.
The neutral must be insulated AFAIK, but the EGC does not need to be.
I am not sure whether that means that you can legally replace that feeder with an identical one which is now non-compliant.This is replacing an existing 3 wire feeder. It was legal when it was installed years ago.
I am not sure whether that means that you can legally replace that feeder with an identical one which is now non-compliant.
Are you wondering whether you can replace the three insulated wires with two insulated and one insulated because the second configuration was legal that the time of installation? It seems to me that you are running afoul of the provision that following the original code from time of installation must still not decrease the safety of the resulting installation.
So, really you are asking two questions:
1. Is like replacement permitted in a non-conforming existing installation?
2. Does going to an uninsulated neutral decrease the safety of the existing grandfathered installation?
Along the same lines, just as a thought exercise, could you install new knob and tube wiring to replace damaged existing k&t?
consider quadraplex, insulated -- hot, hot, neutral; uninsulated -- geounding