Goat

New member
Using overhead lines to an outbuilding, pool, etc, can we use trees as an intermediate and/or final support? Goat.
 
I am reasonably certain that this is not allowed. But I do not keep a code book at home, so I cannot cite the relevant paragraph. Basically, the article says that no living thing can be used to support wires.
 
charlie b said:
I am reasonably certain that this is not allowed. But I do not keep a code book at home, so I cannot cite the relevant paragraph. Basically, the article says that no living thing can be used to support wires.
How long does it take to kill a tree? :cool:
 
Art. 225.26 Vegetation as Support. vegetation such as trees shall not be used for support of overhead conductor spans.

I know that light fixtures and associated equipment are allowed to be supported by trees art.410.16(H).
 