I'm not sure I'm allowed to post here. I am not currently an electrician but I was a residential electrician for 6 years back in mid/late 1980s. I know a lot has changed but I find it hard to believe that AL isn't permitted any longer in an overhead service entrance in RMC for 200A. I am contracting out some home upgrades instead of doing it myself and have a contractor saying that only copper is allowed for the service entrance. It seems like a 4/0 AL would be fine.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The NEC does not prohibit AL service conductors but some power companies will not connect to AL service conductors.
 

jap

Senior Member
Occupation
Electrician
That's a new one on me.

How can they not connect to AL Service conductors when that's what they most commonly use for service conductors?


JAP>
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Some of our POCOs have unusual rules many of which date back so far none of the current folks know the reason....
The one that only accepts Cu requires 3/0 on 200 amp services and all raceways ahead of the service disconnect must be metallic.
I argued unsuccessfully for years that the rules were beyond their jurisdiction
 

rstewart868

Member
Location
Los Angeles
Occupation
Cloud Systems Engineer
I did just confirm with the power company, AL is just fine. I'm stumped why he would claim it's not allowed. There are very few local amendments, I see nothing related to SE conductors.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
This is required in Los Angeles County.
 

Attachments

  • Los Angeles County - Dept of Public Works, Service .pdf
    541.7 KB · Views: 18

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I ran into the same problem with a utility company the next county over, many years ago. They were also the inspection department. They would not allow aluminum for mobile home feeders. They wanted copper all the way, where they connected at the weatherhead with aluminum!
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Sometimes a person may remember something he heard from inspector or another electrician and not realize they were wrong
Lots of shirt pocket rules get made up and evolve through this. I've just moved to a new jurisdiction and yes there are different amendments here but its crazy how bad alot of the electricians I've interacted with who are unaware either of the local amendments for the state which again some are new or non even amended NEC violations. Lots of silly stuff happens when people don't look outside their bubble. But in the end copper isn't as expensive vs AL as it was prepandemic so the cost difference might not be as bad currently.
 