Mattlong317
Member
- Location
- Beech Grove, Indiana
I have done my share of service upgrades, yet oddly enough I have never ran into this issue. I will be starting a 200 Amp service upgrade in 2 days , I bid the job , acquired most of materials, got the permit, and scheduled the service disconnect through Duke energy.
So the bad part, a possible code violation, I believe , and a possibility of not being able to get the service back on at the end of the day , either because the inspector calls this violation or Duke Energy decides it's against their policy or whatever versions of codes they follow.
The problem situation that has dawned on me in the 4th quarter here. The home has an overhead service drop already connected and being used by homeowner for some years now. I am to upgrade the service to 200 amps. Sometime in the recent past the homeowner built a nice patio, with a roof completely covering the patio that spans the entire back of the house . The roof of said patio extends at least 10 feet from the house and is shingled and basically tied into the main house roof seamlessly, although I am not sure how it was framed and stuff , I believe the porch roof is supported by pillars and not attached to the main house, and just to get all the details across the porch/ patio has no walls or doors , barring the back brick wall of the pre existing main house.
Question: Nec code 230 ( I think ) pretty obviously states no more than 6 feet off service drop conductors shall pass over a roof , in an overhead service, so does this apply in all situations ? Question 2: Does this include prexisting structures and code violations that already exist , in the 6 foot scenario mentioned? Question 3: When the code states roof, would this include a porch roof , Or porch roof that was added well after the service was established to begin with?
So after all that being said the riser will be approximately 10 feet from the edge of the porch roof and there will be way more than 6 feet of service drop conductors traveling across this porch roof . And just to be clear the meter is attached to the back brick wall of the house and the riser is going through the original, normal roof overhang. And if it may make a difference the main roof is 4/12 pitch and the added in porch roof is pretty much flat as a roof can be , barely slopes down .
This is my first working with either the county inspector who must tag the meter for reconnect, and Duke Energy, never worked in this county at all, so have no clue of how lax they may be or the pet peeves they may have. Also the there are no easy locations to move the meter base at all , especially due to Windows , doors etc, it would easily be 30/ 40 foot move just to be in a violation free area.
Thank you in advance and I apoligize for rambling , or over detailing the situation.
So the bad part, a possible code violation, I believe , and a possibility of not being able to get the service back on at the end of the day , either because the inspector calls this violation or Duke Energy decides it's against their policy or whatever versions of codes they follow.
The problem situation that has dawned on me in the 4th quarter here. The home has an overhead service drop already connected and being used by homeowner for some years now. I am to upgrade the service to 200 amps. Sometime in the recent past the homeowner built a nice patio, with a roof completely covering the patio that spans the entire back of the house . The roof of said patio extends at least 10 feet from the house and is shingled and basically tied into the main house roof seamlessly, although I am not sure how it was framed and stuff , I believe the porch roof is supported by pillars and not attached to the main house, and just to get all the details across the porch/ patio has no walls or doors , barring the back brick wall of the pre existing main house.
Question: Nec code 230 ( I think ) pretty obviously states no more than 6 feet off service drop conductors shall pass over a roof , in an overhead service, so does this apply in all situations ? Question 2: Does this include prexisting structures and code violations that already exist , in the 6 foot scenario mentioned? Question 3: When the code states roof, would this include a porch roof , Or porch roof that was added well after the service was established to begin with?
So after all that being said the riser will be approximately 10 feet from the edge of the porch roof and there will be way more than 6 feet of service drop conductors traveling across this porch roof . And just to be clear the meter is attached to the back brick wall of the house and the riser is going through the original, normal roof overhang. And if it may make a difference the main roof is 4/12 pitch and the added in porch roof is pretty much flat as a roof can be , barely slopes down .
This is my first working with either the county inspector who must tag the meter for reconnect, and Duke Energy, never worked in this county at all, so have no clue of how lax they may be or the pet peeves they may have. Also the there are no easy locations to move the meter base at all , especially due to Windows , doors etc, it would easily be 30/ 40 foot move just to be in a violation free area.
Thank you in advance and I apoligize for rambling , or over detailing the situation.
Last edited: