I will do soon do an 200Amps overhead electrical service.I will use 3" conduit riser through roof.I had an inspector on a job and he said that Comed doesn't accept roof attachment any more.He advice me to use aluminium conduit which is fine for me.But there is a note in the comed red book that riser is "rigid steel conduit".On web of americanconduit.com I found this notes:"If you’re not familiar with aluminum conduit, you might be wondering, “Does rigid aluminum conduit meet the same code requirements as rigid steel conduit?” The answer is yes – it definitely does".
So may I use an aluminium 3" conduit as a riser?Thank you.
I will do soon do an 200Amps overhead electrical service.I will use 3" conduit riser through roof.I had an inspector on a job and he said that Comed doesn't accept roof attachment any more.He advice me to use aluminium conduit which is fine for me.But there is a note in the comed red book that riser is "rigid steel conduit".On web of americanconduit.com I found this notes:"If you’re not familiar with aluminum conduit, you might be wondering, “Does rigid aluminum conduit meet the same code requirements as rigid steel conduit?” The answer is yes – it definitely does".