225.11 Circuit Exits and Entrances.
Where outside branch and feeder circuits leave or enter a building, the requirements of 230.52 and 230.54 shall apply.
230.54 (F) Drip Loops. Drip loops shall be formed on individual conductors. To prevent the entrance of moisture, service-entrance conductors shall be connected to the service-drop conductors either (1) below the level of the service head or (2) below the level of the termination of the service-entrance cable sheath.
300.8 (D) Locations Exposed to Direct Sunlight. Insulated conductors or cables used where exposed to direct rays of the sun shall comply with one of the following:
(1) Cables listed, or listed and marked, as being sunlight resistant
(2) Conductors listed, or listed and marked, as being sunlight resistant
(3) Covered with insulating material, such as tape or sleeving, that is listed, or listed and marked, as being sunlight resistant
I hope this is what you are looking for.