Maybe someone can point me to the applicable code section -
I'm designing a service entrance which would have an overhead section (75+ feet) from a pole mounted xfmr to a second pole and then an underground section (125+ feet) to the building service (400 amp, single phase). Underground wire sizing would be two runs of 250 MCM AL. Assuming that I'll just have to carry that overhead as well? Or is there a way to back off to the 2/0 AL from Table 310.15(B)(17) on each run once I get overhead?
Haven't checked the voltage drop yet, but that would just end up bumping the wire size on both if needed.
Thanks
I'm designing a service entrance which would have an overhead section (75+ feet) from a pole mounted xfmr to a second pole and then an underground section (125+ feet) to the building service (400 amp, single phase). Underground wire sizing would be two runs of 250 MCM AL. Assuming that I'll just have to carry that overhead as well? Or is there a way to back off to the 2/0 AL from Table 310.15(B)(17) on each run once I get overhead?
Haven't checked the voltage drop yet, but that would just end up bumping the wire size on both if needed.
Thanks