I have always seen a splice right at the weather head. From the utility wire to the customers wire which is usually copper. Does anyone know if you can run ASCR (aluminum conductor steel reinforced) tri plex down a riser and land it in the meter?
I ask because I am coming back out of the disconnect and running over head to another panal and dont really want to have to spilce on to go down the riser?