Just got a call from a friend during a rain storm. Said no CATV at his house but if he wiggled the wire it would come in. I said no problem, you have bad connection I'll be right over.
When I got there I found outer insulation on the cable from the dip pole was melted and swollen where it meets the first splitter. This splitter was grounded via a #12 to the grounded electrode conductor from the meter. Also noticed a small spark when I reconnected the cable to the splitter.
Do you guys think that there could be a short somewhere in the house that is resulting in current in the grounded electrode conductor and this is causing the connection I replaced to get hot enough to melt the insulation?
Or could there be a current from somewher imposed on the catv line coming into the house?
Is there enough energy in a normal CATV signal to cause enough heat (in a bad connection) to melt the insulation on coax?
I plan to go back in the am with a meter and see if I cam measure a current between the cable and the splitter. Would like to check for a voltage on the ground wire but I am not sure what I should measure across. The grounded electrode conduction is the reference I would normally use.
Thanks for your help
When I got there I found outer insulation on the cable from the dip pole was melted and swollen where it meets the first splitter. This splitter was grounded via a #12 to the grounded electrode conductor from the meter. Also noticed a small spark when I reconnected the cable to the splitter.
Do you guys think that there could be a short somewhere in the house that is resulting in current in the grounded electrode conductor and this is causing the connection I replaced to get hot enough to melt the insulation?
Or could there be a current from somewher imposed on the catv line coming into the house?
Is there enough energy in a normal CATV signal to cause enough heat (in a bad connection) to melt the insulation on coax?
I plan to go back in the am with a meter and see if I cam measure a current between the cable and the splitter. Would like to check for a voltage on the ground wire but I am not sure what I should measure across. The grounded electrode conduction is the reference I would normally use.
Thanks for your help